M1 Support Forum Issue with “water alarm” zone configured as “type 1” (NC) Reply To: Issue with “water alarm” zone configured as “type 1” (NC)

#10193
Brad Weeks

    For a Water Sensor you should be using a Normally Open sensor and install the 2.2KΩ across the contacts so you get the three states Normal secure, Alarm when the contacts short and “Trouble” in the event the loop opens (cut wire for example).