  • #9354
    Neil Heuer

      I have 2 Cosmods for two strings of smoke / co detectors.  The only way to reset them after an alarm is to remove power.  I’ve been told I need to use a relay with an output to cut power on disarm.  I’ve installed the relays for each chain of detectors, but I am unclear about how to program the rule to reset the two strings when an alarm for fire or CO is acknowledged.

      #9360
      Chuck Saffer

        Neil, is this resolved?  We used the “Switched Aux Power” to power the Cosmods.  The smoke reset function will reset the detectors.

        #9361
        Neil Heuer

          I installed 2 relays on outputs 8 and 9. What im unclear about is how and when to trip the relay (on for 2 seconds).

          #9617
          William Turner

            I didn’t need relays.   Used the “switched aux power” as Chuck indicated.   Perhaps there’s a good diagram for setting these up with an Elk M1G for those that are integrating them?

            #9636
            Chuck Saffer

              Neil, if this has not been resolved.  We use 2-outputs, 1 for smoke trigger; 1 for CO Trigger.  The rules are “When a fire (or CO) is in alarm”, “Then turn on output #, for 12 minutes”.  We add a rule to turn off the output if the alarm is turned off.  I hope this helps.