I have 2 Cosmods for two strings of smoke / co detectors. The only way to reset them after an alarm is to remove power. I’ve been told I need to use a relay with an output to cut power on disarm. I’ve installed the relays for each chain of detectors, but I am unclear about how to program the rule to reset the two strings when an alarm for fire or CO is acknowledged.
I didn’t need relays. Used the “switched aux power” as Chuck indicated. Perhaps there’s a good diagram for setting these up with an Elk M1G for those that are integrating them?
Neil, if this has not been resolved. We use 2-outputs, 1 for smoke trigger; 1 for CO Trigger. The rules are “When a fire (or CO) is in alarm”, “Then turn on output #, for 12 minutes”. We add a rule to turn off the output if the alarm is turned off. I hope this helps.