M1 Support Forum ELK M1XEP Keypad/Keystroke process to add wireless smoke detector

Viewing 9 posts - 1 through 9 (of 9 total)
  • Author
    Posts
  • #9940
    Jason Roberts

      What is the keypad/button presses to add a wireless smoke detector?

      M1XEP – M1XRF2Hv2 – M1XP keypad

      #9941
      Brad Weeks

        Are you able to connect to the system using the ElkRP2 software? If so you can learn in a wireless device from ElkRp2 if you have the Honeywell serial number. From keypad programming:

        • Press the ELK key, screen should display 1-View/Control Automation Fncts
        • Press the 9 key, screen should display 9-Installation Programming (0)
        • Press the right arrow key and you should be prompted “Auth Required Enter Valid PIN — This is the Installer Level Keypad Programming Code
        • Screen should display 01-Bus Module Enrollment
        • Type 14, screen should display 14-Wireless Setup
        • Press the right arrow key, screen should display 1: Rec Sel {Up/Down symbols} Prg {right arrow symbol} Receiver Options
        • Type 3 and screen should display 3: Learn Sel {Up/Down symbols} Prg {right arrow symbol} Wireless Transmtr
        • Press the Right Arrow key
        • Type in the 3 digit zone number for the zone you want to learn in and press the right arrow key
        • Screen will display WZone = xxx (xxx= the zone number to learn in) TransmitrToLrn
        • Press the right arrow key
        • Insert the battery into the sensor or trip the tamper switch or move the magnet away from the sensor
        • When Learned In you should hear a chime from the keypad and the keypad screen will advance to the next available wireless zone
        • Press the ELK Key to save

        Additional information can be found starting on page 47 of the M1 Installation Manual and within the M1XRF2Hv2 Installation Manual

        #9943
        Jason Roberts

          Is the Honeywell serial number in the receiver box or where is it?

          I can connect to the M1Xep through ELKrp.

          Can you please give the process through ELKrp? I believe through Rp will be easier?

          #9944
          Brad Weeks

            The Honeywell serial number is a 7 digit number located on the wireless sensor.

            Have you enrolled the M1XRF2H?

            Have you created a Wireless Group in ElkRP2?

            If so:

            • Under Zone (Inputs) click on your Wireless Group x
            • Click on the zone number you want to configure
            • Set the Zone Definition, Type and any other option you need to select
            • Click “Wireless Setup”
            • Check “Enabled”
            • Supervised will either be 0 = Not Supervised for FOBs, 1 = Normal Supervision for Window/Door, 3 = Fire Supervision for Smoke Detectors
            • In the H ID box enter the 7 digit serial number for the Honeywell Wireless Sensor
            • In most cases the LOOP will equal 1 or reference the Honeywell instructions for the LOOP setting
            • Click SAVE and Close the “Change Wireless Zone” window
            • From the Zone page click “Send to Control” or “Send and Say”
            #9949
            Jason Roberts

              Thank you.

              • From what I see, the Loop should be 2 for smoke detectors – can you please confirm the loop number again? I will also look at the Honeywell instructions.
              • Also, once the H ID is entered, what happens in Tx ID and DL?
              #9957
              Brad Weeks

                In most cases the LOOP will be 1 for the Honeywell compatible smoke detectors. When you enter the Honeywell serial number in the H ID field the TxID and DL will automatically fill in.

                #9958
                Jason Roberts

                  Should have asked this earlier – once the serial is entered in H ID and saved – at what point is the tab pulled to activate the a batteries? And test?

                  #9959
                  Brad Weeks

                    After the zone is completely configured Zone Def, Type, Wireless Setup, Enabled Checked, LOOP and H ID entered then remove the battery tab and test

                    #9972
                    Jason Roberts

                      Thank you. Can you please confirm the settings?

                      Configuration

                      • Definition is 10 Fire Alarm
                      • Type (auto selected) is 5 = Fire/4-Wire Smoke RF
                      • Atttributes is All Left Unchecked

                      Wireless Setup

                      • Enabled is Checked
                      • Supervised is 3 = Fire Supervision
                      • H ID entered and Tx ID and Dl auto populated
                      • Loop is 1
                    Viewing 9 posts - 1 through 9 (of 9 total)