February 4, 2026 at 6:45 pm #9940Jason Roberts
What is the keypad/button presses to add a wireless smoke detector?
M1XEP – M1XRF2Hv2 – M1XP keypad
February 5, 2026 at 11:19 am #9941Brad Weeks
Are you able to connect to the system using the ElkRP2 software? If so you can learn in a wireless device from ElkRp2 if you have the Honeywell serial number. From keypad programming:
- Press the ELK key, screen should display 1-View/Control Automation Fncts
- Press the 9 key, screen should display 9-Installation Programming (0)
- Press the right arrow key and you should be prompted “Auth Required Enter Valid PIN — This is the Installer Level Keypad Programming Code
- Screen should display 01-Bus Module Enrollment
- Type 14, screen should display 14-Wireless Setup
- Press the right arrow key, screen should display 1: Rec Sel {Up/Down symbols} Prg {right arrow symbol} Receiver Options
- Type 3 and screen should display 3: Learn Sel {Up/Down symbols} Prg {right arrow symbol} Wireless Transmtr
- Press the Right Arrow key
- Type in the 3 digit zone number for the zone you want to learn in and press the right arrow key
- Screen will display WZone = xxx (xxx= the zone number to learn in) TransmitrToLrn
- Press the right arrow key
- Insert the battery into the sensor or trip the tamper switch or move the magnet away from the sensor
- When Learned In you should hear a chime from the keypad and the keypad screen will advance to the next available wireless zone
- Press the ELK Key to save
Additional information can be found starting on page 47 of the M1 Installation Manual and within the M1XRF2Hv2 Installation Manual
February 5, 2026 at 6:03 pm #9943Jason RobertsIs the Honeywell serial number in the receiver box or where is it?
I can connect to the M1Xep through ELKrp.
Can you please give the process through ELKrp? I believe through Rp will be easier?
February 5, 2026 at 6:30 pm #9944Brad Weeks
The Honeywell serial number is a 7 digit number located on the wireless sensor.
Have you enrolled the M1XRF2H?
Have you created a Wireless Group in ElkRP2?
If so:
- Under Zone (Inputs) click on your Wireless Group x
- Click on the zone number you want to configure
- Set the Zone Definition, Type and any other option you need to select
- Click “Wireless Setup”
- Check “Enabled”
- Supervised will either be 0 = Not Supervised for FOBs, 1 = Normal Supervision for Window/Door, 3 = Fire Supervision for Smoke Detectors
- In the H ID box enter the 7 digit serial number for the Honeywell Wireless Sensor
- In most cases the LOOP will equal 1 or reference the Honeywell instructions for the LOOP setting
- Click SAVE and Close the “Change Wireless Zone” window
- From the Zone page click “Send to Control” or “Send and Say”
February 9, 2026 at 11:53 am #9949Jason RobertsThank you.
- From what I see, the Loop should be 2 for smoke detectors – can you please confirm the loop number again? I will also look at the Honeywell instructions.
- Also, once the H ID is entered, what happens in Tx ID and DL?
February 9, 2026 at 3:58 pm #9957Brad Weeks
In most cases the LOOP will be 1 for the Honeywell compatible smoke detectors. When you enter the Honeywell serial number in the H ID field the TxID and DL will automatically fill in.
February 9, 2026 at 4:06 pm #9958Jason RobertsShould have asked this earlier – once the serial is entered in H ID and saved – at what point is the tab pulled to activate the a batteries? And test?
February 9, 2026 at 4:23 pm #9959Brad Weeks
After the zone is completely configured Zone Def, Type, Wireless Setup, Enabled Checked, LOOP and H ID entered then remove the battery tab and test
February 10, 2026 at 10:10 am #9972Jason RobertsThank you. Can you please confirm the settings?
Configuration
- Definition is 10 Fire Alarm
- Type (auto selected) is 5 = Fire/4-Wire Smoke RF
- Atttributes is All Left Unchecked
Wireless Setup
- Enabled is Checked
- Supervised is 3 = Fire Supervision
- H ID entered and Tx ID and Dl auto populated
- Loop is 1
-