      I have M1G with M1XRF2H receivers and Honeywell 5890 motions sensors running fine for years.

      Recently, 1 zone has been throwing an error: (and monitoring station calls)
      <table>
      <tbody>
      <tr>
      <td>9</td>
      <td>Tue 11/28/2023</td>
      <td>14:00</td>
      <td>2</td>
      <td>1381 = TRANSMITTER SUPERVISION LOSS</td>
      <td>CAB LAVATORY (Zn 34)</td>
      </tr>
      </tbody>
      </table>
      after replacing the batteries, it runs fine for a few days, then does it again,Under status it says something like “transmission lost” and under State it said “Short(-)”. So I figured sensor is going bad, so I replaced it and re-enroled the system and now status says “Normal” but State says “N/A..

      What do you make of this?

      #7564
      Brad Weeks

        Sounds like the original sensor may have been  defective. You noticed the Status N/A under the Status Window? If so open / close or trip the motion several times which should update the screen.

        #7565
        James Thornburg

          Thanks Brad,

          Turns out batts on replacement sensor were tired, all good now