  • #7219
    Robert Little

      Can someone verify the settings for this on a M1G?  I have 2 of these up on the data bus hub as data module 6 and 7.  Are the A/C and Battery notifiers RF/wireless?  It appears that #6 virtually connects to Zone 198 and #7 to Zone 199.  If that is correct, then do I need to hardwire the AC trouble relay on the P212S to a different zone?  Thanks!

      #7223
      Brad Weeks

        If the ELK P212S Supervised Power Supply is connected to the M1’s Data Bus and set to M1 Mode (jumper between NEG and “M1 Mode Terminal”)  the Definition should be Def – 32 Power Supervisory 24 Hr. The P212S is considered a Keypad Type 1 Bus Device and the address will determine the Zone that will report the AC Fail and Low Battery. In the M1 Mode there is no need to wire the AC Trouble Relay to a Zone.

        #7233