Fire Alarm to Relay output

M1 Support Forum Fire Alarm to Relay output

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #10379
    Darren Schotte

      I am sorry if this is in the wrong area.  The company I work for just took on a small project to use the ELK-M1EZ8 with smoke detectors.  They purchased the ELK-M1EZ8KBS system.  I have managed to wire the 4-wire Fire Alarm devices and program zone 1 as a fire zone. I can get the Fire Alarm and Trouble to function as expected.  For this issue, I believe we need additional parts, and I cannot prove to my manager that I need them.   I need to be able to program the outputs to trigger a relay that notifies an internal system of a fire alarm and/or a Fire system trouble.  Am I correct that I will need the Main Serial interface and the M1RB (relay board) to connect my PC to the board and program the outputs?

      Any help with this is greatly appreciated.

      Thanks

      #10382
      Brad Weeks

        In order to connect ElkRP2 to the M1EZ8 to create the rule(s) you will need the M1EZ8MSI Main Serial Interface https://www.elkproducts.com/product/m1ez8-main-serial-interface-m1ez8msi/ . The M1EZ8MSI provides a Serial port so you can use a USB to RS232 Serial cable and direct connect.