Glass Break Issue - ELK Products

Glass Break Issue

M1 Support Forum Glass Break Issue

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #9707
    Russ Mckenzie

      I have installed 13 x FG1625FM glass breaks, hardwired to a zone expander on the M1Gold powered by an additional Atronics 12v power supply. There are also a couple motions on the expander that work fine so there is no problem with the expander itself or power.
      The GB’s have power to them as the LED light does flash when testing.
      The issue is, in the RP2 software, they are identifying as having an EOL resistor and are only ‘normal’ when configured as such. – I did NOT install EOLR’s.
      They are tampered in both NC (which is what I have configured these to on this system in the past without issue) and NO. Also EOL Supervised on Short & Open.
      The wiring is correct and are all programmed as 03-Burglar Perimeter Instant and sent to control.
      What could be the issue?

      #9708
      Brad Weeks

        Do you have common DC Negative between the the Altronix Power Supply and any NEG on the M1? In ElkRP2 under Status what is the Voltage Level for the Zone?

         