M1 Support Forum Undocumented (or bug) in ASCII AS message

Viewing 6 posts - 1 through 6 (of 6 total)
  • Author
    Posts
  • #8689
    Glenn Waters

      When using the ASCII protocol to get alarm status from the panel the following message is received (spaces added for readability):

      1EAS 01010000 04041111 U0000000 00E3

      The “U” is not documented in the ASCII protocol documentation. The person reporting this issue says that they don’t (yet) have a battery on the panel, could the “U” stand for “unsupervised”?

      #8694
      Brad Weeks

        Are any of the Burg Zones in Area 1 in a Trouble State or programmed with “Periodic Trip” enabled?

        #8695
        Glenn Waters

          I’m unsure as the problem seems to have resolved. Can you clarify if “U” is valid in the ASCII Alarm Status message and what “U” stands for?

          #8701
          Glenn Waters

            So the problem has reoccurred and there is a zone in troubled state.

            #8708
            Brad Weeks

              At this time it isn’t documented M1 RS232 Protocol but the ‘U’ matches up with the “SecurityAlert” alarm in the M1’s Alarm Type Table.

              #8710
              Glenn Waters

                I looked through all the docs (installation and user guide) but did not find the Alarm Type Table. Where should I look?  Thanks!