Adding wireless to existing M1

› M1 Support Forum › Adding wireless to existing M1

Viewing 2 posts - 1 through 2 (of 2 total)
  • Author
    Posts
  • #4983
    Bob Hoevenaars

      Since the first receiver must be address 2, what is the best approach when adding wireless capabilities to an existing hardwired only system.  Is there a way to do this so that you don’t have to shift all the zones up 16 addresses?

      #4984
      Brad Weeks

        Assign the M1XIN to a new address depending on how many wireless sensors you need to add — for example set the M1XIN from existing Address #2 to Address #6 then connect the M1XRFTWM at address #2 and perform the Bus Module Enrollment. Next you will need to Delete Hardwired Group 2 and recreate those zones starting at Zone 81 (M1XIN Address #6), create Wireless Group 2 and start your Wireless Zones at #17

         

      Viewing 2 posts - 1 through 2 (of 2 total)
      • You must be logged in to reply to this topic.