M1 Support Forum M1ZTS Not All Input Zones Displaying on Keypads

Tagged: 

Viewing 4 posts - 1 through 4 (of 4 total)
  • Author
    Posts
  • #5723
    Jon Gonzales

      I have 7 M1ZTS installed on M1G input zones 1-7.  All are set for #33 temp, fast loop response and global loop response set for 40ms.  Only zone 1 is available (default display when in temp sensors) for selection/viewing on the keypad, no others can be selected.  I have validated M1ZTS’s are receiving over 13vdc of power, all have the same led indicator flashes. When I observe in RP current status,  all 7 zones have an open voltage of approx 13.7vdc and cycle between shorted .6vdc and back to open voltage reading.  What am I missing?

      Thank You

       

      #5726
      Brad Weeks

        Are you using the M1KPNAV Keypad? If so press Menu, press Next Page, press Synchronize , press Start. Once complete then under Menu, Automation, Temperature Sensors see if temp sensors 1-7 show

        #5728
        Jon Gonzales

          Yes using the M1KPNAV Keypad and all temp zones are displaying after following the sync instructions.  Thank you!

          #8611
          Philip Platt

            I have a temp sensor that seems to be now flashing the internal status LED red for some reason but i cannot find any user manual for it that explains the status led.

            Should the led normally flash red? I don’t believe it always has done this as the customer is stating that it is quite bright.

          Viewing 4 posts - 1 through 4 (of 4 total)
          • You must be logged in to reply to this topic.
          Scroll to Top