M1 Support Forum Thermostats not enabled on keypad

Viewing 2 posts - 31 through 32 (of 32 total)
  • Author
    Posts
  • #6195
    Trenton Wilson

      okay I tried this Variance that you listed

      and all it did was become non responsive

      • Jumpers S5 – S8 — S5 UP (1), S6 down (0), S7 UP (1), S8 down (0)
      #6239
      Brad Weeks

        Update all thermostats are now reporting using the following steps:

        • Factory Defaulted the thermostats
        • Set the Network Nodes to 16
        • Set the Address of each thermostat 1-7
        • Set the Baud Rate to 9600
        • Set 7-Day Programming to Non-programming mode (Option 35)

         

      Viewing 2 posts - 31 through 32 (of 32 total)